Question: Is there an NFPA restriction regarding the application of an Emergency Generator that is designated for Life Safety Systems, concerning whether or not it can also have other loads on it that are not Life Safety Systems?
Yes, there is an NFPA restriction regarding the application of an Emergency Generator that is designated for Life Safety Systems.
NFPA 70: National Electrical Code (NEC) Article 700.12(D) states that "Emergency generators shall not be used to supply loads other than those connected to the emergency system."NFPA 110: Standard for Emergency and Standby Power Systems Section 5.3.
1.2 states that "Emergency generators shall be dedicated to serving the electrical needs of the protected premises and shall not be used to supply other loads."Exceptions to the Rule
In some cases, exceptions to the rule may be allowed, but only with specific approval from the authority having jurisdiction (AHJ).
NFPA 70: NEC Article 700.12(D) Exception No. 1 allows emergency generators to supply loads that are "necessary for the safe operation of the facility." This exception is typically interpreted to include loads such as fire pumps, elevator control systems, and ventilation systems. NFPA 110: Standard 5.3.
1.2 Exception allows emergency generators to supply "standby loads" that are "essential to the safe operation of the facility." This exception is similar to the exception in NFPA 70, but it may be interpreted more broadly to include loads such as lighting and communications systems.
Reasoning for the Restriction:
The purpose of the restriction is to ensure that emergency generators are available to power Life Safety Systems during a power outage. If the generator is also supplying non-Life Safety loads, it may not be able to provide the necessary power to the Life Safety Systems when needed. Flag for review