Topic: EMT Support

User: augie47, Location: Tennessee

Asked on: Wednesday, February 2, 2011 at 7:37 pm EST
Answered on: Tuesday, May 14, 2024 at 1:05 am EDT

Question: Art 358 States:"(A) Securely Fastened. EMT shall be securely fastened in place at least every 3 m (10 ft). In addition, each EMT run between termination points shall be securely fastened within 900 mm (3 ft) of each outlet box, junction box, device box, cabinet, conduit body, or other tubing termination."Is a coupling considered a "tubing termination" ? Specifically, if one has a3/4 rigid 90 stubbed from a slab then transitioned to EMT, does the EMT have to be strapped with 3 ft of the transition ?

Yes, a coupling is considered a "tubing termination" according to the definition in Article 100 of the National Electrical Code (NEC).

Definition of Tubing Termination:"A connection point between two or more lengths of the same type of raceway."Therefore, the EMT must be securely fastened within 3 ft of the transition coupling where it connects to the rigid conduit stub. Flag for review