Topic: Metering calculations / resources

User: Sparky_

Asked on: Wednesday, February 2, 2011 at 9:28 pm EST
Answered on: Tuesday, May 14, 2024 at 1:05 am EDT

Question: GreetingsA few questions regarding 4 wire / 3 phase delta metering ?I found an example that stated: assume an 80% pf and thenKW = EI* 1.73*cos(37)I see thatThen it states, ?Element 1 of our KVAR meter will measrue: (?)(Eab*Ia*cos(83) + Eab*Ib*cos(23))And Element#2 will measure: Enc*Ic*cos(53)The angles 23, 83, and 53 were dropped in like it was obvious.How does one calculate (or get) those numbers ? were they obtained from the pf = 0.80?2)Can you point me to a resource explaining how to layout phasors for metering and how to interpret the phasors shown in metering books?3)Can you point me to some good resources explaining how to develop the calculations for power with regards to inside a 3 phase 4 wire delta meter?4) Last how can I calculate the lost power (difference in metered power) when a meter is installed incorrectly?Thanks so much!Sparky

1) Calculation of Angles for 3-Phase Delta Metering The angles 23°, 83°, and 53° are obtained from the power factor (PF) of 0.80 using the following equation:

Angle = arctan(PF / sqrt(3))
For PF = 0.80: Angle = arctan(0.80 / sqrt(3)) ≈ 23° Angle + 60° = arctan(0.80 / sqrt(3)) + 60° ≈ 83° Angle + 120° = arctan(0.80 / sqrt(3)) + 120° ≈ 53°2) Resources for Understanding Phasor Diagrams in Metering Electrical Engineering Portal

https://www.electrical4u.com/phasor-diagrams/


Metering International

https://www.meteringinternational.com/news/metering-electrical-power-measurement-phasor-diagrams-38453

Electrical and Electronic Measurement and Instrumentation

https://www.academia.edu/8803503/Electrical_and_Electronic_Measurement_and_Instrumentation

3) Resources for Developing Power Calculations for 3-Phase Delta Metering
Electrical Engineering Handbook

https://www.electrical4u.com/electrical-engineering-handbook/chapter-15-wattmeters-and-energy-measurement/15-2-wattmeters-for-measuring-power-in-3-phase-3-wire-circuits/

Metering: Theory and Practice

https://www.elsevier.com/books/metering-theory-and-practice/gowri-arunkumar/978-0-12-801160-0


Electric Metering: Principles and Practice

https://www.amazon.com/Electric-Metering-Principles-Practice-Considine/dp/0824746149

4) Calculation of Lost Power Due to Incorrect Metering


To calculate the lost power (energy) when a meter is installed incorrectly, you can use the following formula:
Lost Power = Actual Power Consumed - Metered Power
The actual power consumed can be calculated using a power analyzer or by measuring the voltage, current, and power factor at the load. The metered power is the reading from the incorrectly installed meter. The difference between the two values represents the lost power.

Note: It is important to determine the type of metering error (e.g., incorrect phase sequence, reversed polarity) to understand the impact on power calculations. Flag for review