Question: HiiI have a small confusion regarding 3-phase wye circuit.this circuit is for heating system in CB control cubicle. the suppy for the circuit is 380/220 V AC and value of each resistor is 800Ohms
3-Phase Wye Circuit
In a 3-phase wye circuit, the three phases are connected at a common neutral point. The line-to-line voltage is the supply voltage, while the line-to-neutral voltage is √3 times less than the line-to-line voltage.
Given Parameters
Supply voltage: 380/220 V AC Resistor value: 800 Ohms Wye configuration
Calculations
Line-to-Neutral Voltage (V_LN)V_LN = V_LL / √3 = 220 V / √3 = 127 V
Current (I)I = V_LN / R = 127 V / 800 Ohms = 0.159 A
Power (P)P = I^2 R = 0.159 A^2 800 Ohms = 20.15 W
Total Power (P_total)
Since there are three resistors in the circuit, the total power is three times the power of each resistor:P_total = 3 P = 3 20.15 W = 60.45 W
Conclusions: The line-to-neutral voltage in the circuit is 127 V. The current flowing through each resistor is 0.159 A. The power dissipated by each resistor is 20.15 W.* The total power dissipated by all three resistors is 60.45 W. Flag for review