Topic: Current flowing in neutral of a 3 phase wye circuit of a Herater in Circuit Breaker

User: Karthik_venna, Location: UK

Asked on: Thursday, February 3, 2011 at 8:46 am EST
Answered on: Thursday, May 23, 2024 at 5:37 pm EDT

Question: HiiI have a question regarding Heater circiut of circuitbreaker control cubicleThe circuit is fed with 380/220V with having resistors of 800 Ohms in each leg.

Heater Circuit in Circuit Breaker Control CubicleCircuit Description

The heater circuit is powered by a 380/220V three-phase supply. Each phase of the supply is connected to an 800-ohm resistor.

Purpose of Heater Circuit

The heater circuit provides a constant heating current to the circuit breaker trip coils. This current maintains a constant trip temperature, ensuring accurate tripping of the circuit breaker when necessary.

Circuit Analysis



Phase Voltages

The phase voltages (V) are: V1 = V2 = V3 = 220V (line-to-neutral)

Resistor Current

The current (I) flowing through each 800-ohm resistor is: I = V / R = 220V / 800Ω = 0.275A

Power Dissipated by Resistors

The power (P) dissipated by each resistor is: P = I^2 R = (0.275A)^2 800Ω = 60.125W

Total Power Consumption

The total power consumption of the heater circuit is: P_total = 3 P = 3 60.125W = 180.375W

Notes:
The resistors in the heater circuit are typically wire-wound or ceramic elements. The resistance value of the resistors is chosen to provide the desired trip temperature and trip time characteristics of the circuit breaker.* The heater circuit should be properly sized to ensure sufficient heating current for accurate tripping of the circuit breaker. Flag for review