User: jtinge, Location: Hampton, VA
Asked on: Thursday, February 3, 2011 at 11:29 am EST
Answered on: Tuesday, May 14, 2024 at 1:07 am EDT
Question: Are joints, taps, and terminal connections considered non-sparking or non-arcing when applying NEC 501.10(B)(4), which does not require boxes and fittings to be explosion-proof if they do not contain any arcing devices. "Electrical Installations in Hazardous Locations", by Schram and Earley, states that non-sparking equipment includes splices in junction boxes, under the discussion of Class 1, Div 2 wiring methods. This seems to contradict the way joints, taps, and terminal connections are treated in Class 2, Div 2 environments. Can anyone shed some light on this?
Scope of NEC 501.10(B)(4)
NEC 501.10(B)(4) is specifically applicable to Class I, Division 2 hazardous locations. It states that boxes and fittings enclosing devices that do not contain any arcing or sparking contacts, such as switches, circuit breakers, fuses, receptacles, and motor controllers, shall not be required to be explosion-proof.
Non-Sparking Equipment in Class 1, Division 2 Locations
As mentioned in the reference text "Electrical Installations in Hazardous Locations," splices in junction boxes can be considered non-sparking equipment in Class 1, Division 2 locations. This is because the connections are made without arcing or sparking.
Joints, Taps, and Terminal Connections in Class 2, Division 2 Locations
The treatment of joints, taps, and terminal connections in Class 2, Division 2 locations is different from that in Class 1, Division 2 locations. According to NEC 501.10(B)(3), the terminals of motors, generators, and transformers, and the terminals of other equipment where the arcing, sparking, or heating of terminals may ignite the atmosphere, shall be enclosed in explosion-proof enclosures.This is because Class 2, Division 2 locations are where flammable gases or vapors are likely to be present in unusually high concentrations under normal operating conditions. The terminals of motors and other equipment can generate sparks or heat that could ignite these flammable gases or vapors.
Conclusion
While joints, taps, and terminal connections may be considered non-sparking in Class 1, Division 2 locations, they are required to be enclosed in explosion-proof enclosures in Class 2, Division 2 locations because of the higher risk of ignition in these areas. Flag for review