User: Rockey, Location: Logan, Utah
Asked on: Thursday, February 3, 2011 at 12:02 pm EST
Answered on: Tuesday, May 14, 2024 at 1:07 am EDT
Question: New 277/480 3phase Service/ Switchboard were our conduits and feeder was intended underground but distroyed so now overhead conduits and Service conductor are to be installed. They will cross the secondary bussbar of the main switch. These conductors come straight from the utility Transformer (unfused). I know its not industry standard but I can not find in 230 where they restrict you to cross Line and Load?
NEC Article 230.8 states that "Services shall not be run in the same raceway, cable, box, or cabinet with other conductorsunless the conductors of the other circuits are also for supply to the same building or structure."However, NEC Exception No. 2 to 230.8 states that "Overhead service conductors shall be permitted to pass overbranch-circuit and feeder conductors run outdoors."Therefore, based on this exception, it is permissible to have overhead service conductors cross the secondary bussbar ofthe main switch, as long as the following conditions are met: The service conductors are run outdoors. The service conductors are not run in the same raceway, cable, box, or cabinet with other conductors.It is important to note that this is not industry standard, and it is recommended to follow the manufacturer's instructions for the installation of the service and switchboard. Flag for review