Topic: FMT Bonding on transfer switch

User: john8791, Location: Iowa, US

Asked on: Thursday, February 3, 2011 at 1:52 pm EST
Answered on: Tuesday, May 14, 2024 at 1:07 am EDT

Question: A Reliance brand load-side transfer switch is installed with 18" of FMT (preinstalled with wires run through including an EGC) connected to main panel. The installation would seem to comply with NEC 250.118(5) as the circuits are 20A or less thereby not requiring separate bonding. However, the fitting to the main panel was installed into a 1" knockout that was reduced to 3/4" with reducing washers. Does that change the requirement? Thanks.

Yes, the requirement changes. NEC 250.118(5) requires the bonding jumper to be sized in accordance with 250.
122. NEC 250.122(A) requires the bonding jumper to be sized based on the largest ungrounded conductor connected to the system or to the grounding electrode conductor. In this case, the largest ungrounded conductor is 2 AWG, which requires a bonding jumper sized at 6 AWG. The reducing washers reduce the size of the opening to 3/4", which is too small to accommodate a 6 AWG bonding jumper. Therefore, a separate bonding jumper must be installed. Flag for review