Question: NEC states that the surface temperature of a luminaire in a C1D2 location cannot exceed 80% of the ignition temperature of the gas involved. One reference states that the luminaire surface temperature is measured on the hottest part of the fixture-either inside or outside, but another states that it's the lamp surface temperature not the luminaire surface temperature that must not exceed the 80% gas ignition temperature. Which is the correct interpretation of the code requirement?
The correct interpretation of the code requirement is that the surface temperature of the luminaire, not the lamp, must not exceed 80% of the ignition temperature of the gas involved.NEC 501.9 states that "Luminaires shall not have exposed surfaces that normally exceed 80 percent of the ignition temperature in degrees Celsius of the gas or vapor involved."This means that the surface temperature of the luminaire itself, either inside or outside, must not exceed 80% of the ignition temperature of the gas or vapor in the hazardous location.The lamp surface temperature is not specifically mentioned in the code requirement, but it is important to note that the lamp is a part of the luminaire. Therefore, the lamp surface temperature must also be considered when determining if the luminaire meets the code requirement.If the lamp surface temperature exceeds 80% of the ignition temperature of the gas or vapor involved, then the luminaire is not suitable for use in that hazardous location. Flag for review