Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Transformer Conductor Size

User: blues, Location: Nevada

Asked on: Thursday, February 3, 2011 at 2:36 pm EST
Answered on: Tuesday, May 14, 2024 at 1:07 am EDT

Question: As allowed per Nec 450.3(B) tranformer primary OCPD may be set at 250% of primary current rating provided the secondary is not set no more that 125% of FLC. My question is do the primary conductors need to be sized per the OCPD (250%) and not the FLC of transformer primary plus 125% as I would normally do?Thanks,Dan

Per NEC 450.3(B) the primary conductors would be sized per the 250% of the primary current rating, not the transformer primary plus 125%. Flag for review

Previous Question Next Question