Question: As allowed per Nec 450.3(B) tranformer primary OCPD may be set at 250% of primary current rating provided the secondary is not set no more that 125% of FLC. My question is do the primary conductors need to be sized per the OCPD (250%) and not the FLC of transformer primary plus 125% as I would normally do?Thanks,Dan
Per NEC 450.3(B) the primary conductors would be sized per the 250% of the primary current rating, not the transformer primary plus 125%. Flag for review