User: baddriver, Location: Tri-Cities, Washington
Asked on: Thursday, February 3, 2011 at 5:36 pm EST
Answered on: Tuesday, May 14, 2024 at 1:07 am EDT
Question: I'm looking for help determining the answer to the following in accordance with the NEC.A 480v 3-phase 400A panel board with a 400A 100% rated main breaker is being installed. It is fed by a 400A 100% rated breaker in an upstream distribution board. The question is about required ampacity of the panel board feeder.From 215.2(A)(1): The minimum feeder-circuit conductor size, before the application of any adjustment or correction factors, shall have an allowable ampacity of not less than the noncontinuous load plus 125 of the continuous load.215.2(A)(1) Exception No 1 allows for sizing the feeders at 100% cont+non cont load since we have 100% rated breakers.What happens if we don't know what the actual connected load will be? Does this allow for a smaller feeder to be installed?For example: If we assumed the connected load was 375A continuous, we could select 500MCM cable rated for 380A and satisfy 215.2(A)(1). Then we could size the overcurrent protective device at 400A 100% rated to satisfy 240.4(B). If we do not know the connected load, could we not use the same sizing as this and select a 500MCM cable rather than a 600MCM and satisfy code? Does the code have any language that states this is not allowed?
Yes, it is permissible to use a smaller feeder if the actual connected load is unknown.
The NEC does not require knowing the actual connected load to size the feeder. Instead, it allows for an assumed load calculation based on the panelboard rating.In your example: The panelboard rating is 400A. Applying the 100% rule in 215.2(A)(1) Exception No. 1, the minimum feeder ampacity is 400A. The 500MCM cable with an ampacity of 380A satisfies this minimum requirement. The 400A main breaker at the panelboard and distribution board satisfies overcurrent protection.Even though the assumed connected load of 375A continuous is less than the panelboard rating of 400A, the smaller 500MCM feeder is still permitted because it meets the minimum ampacity requirement specified in the code.
NEC Language
The following NEC language supports this interpretation:
215.2(A)(1)
"The minimum feeder-circuit conductor size ... shall have an allowable ampacity of not less than the noncontinuous load plus 125 of the continuous load."
215.2(A)(1) Exception No. 1: "Where one or more 100 percent rated circuit breakers or fuses are used for the protection of the conductors, the feeder conductors shall be permitted to be sized to carry 100 percent of the continuous and noncontinuous load."These sections do not require the exact connected load to be known for feeder sizing. Instead, they allow for an assumed load calculation based on the panelboard rating when using 100% rated overcurrent protection. Flag for review