Topic: Diversity Calculations for Military Dormitory BEQ

User: blvengineers, Location: Ohio

Asked on: Friday, February 4, 2011 at 4:11 am EST
Answered on: Tuesday, May 14, 2024 at 1:08 am EDT

Question: Hello. I am trying to size main feeder and branch feeders for a 4 story military dorm. Here is the distribution. Main service on 1st floor servers 10 individual panels separated by mechanical, lighting and general receptacle loads. On the 2nd, 3rd and 4th floors, there are large distribution panels that serve the same for each floor. Where do I start with diversifying the load? There are approximately 8 dorm units served from each general receptacle panel, about 20 units served from the mechanical panel and 44 from the lighting panels. Approximately the same for each floor. I am having issues understanding how to apply the diversity. For the record, there is no fixed cooking equipment.

Step 1: Determine Base Load

Calculate the peak demand for each type of load (mechanical, lighting, general receptacle) based on the number of units served and their typical loads. For example: Mechanical load

20 units x 1 kW = 20 kW


Lighting load

44 units x 0.5 kW = 22 kW

General receptacle load

8 units x 1.5 kW = 12 kW

Step 2: Apply Diversity Factors
Mechanical load

70% (typical diversity factor for mechanical loads)

Lighting load

50% (typical diversity factor for lighting loads)


General receptacle load

35% (typical diversity factor for receptacle loads)

Step 3: Calculate Diversified Load


Multiply the base load by the corresponding diversity factor: Diversified mechanical load

20 kW x 0.7 = 14 kW


Diversified lighting load

22 kW x 0.5 = 11 kW

Diversified general receptacle load

12 kW x 0.35 = 4.2 kW

Step 4: Determine Total Diversified Load


Sum the diversified loads for all three panels on each floor:
2nd, 3rd, and 4th Floors

14 kW (mechanical) + 11 kW (lighting) + 4.2 kW (general receptacle) =

29.2 kW
Step 5: Size Main Feeder Multiply the total diversified load by the demand factor (typically 1.25 or 1.3): 29.2 kW x 1.25 = 36.5 kW Select a main feeder cable with a current rating greater than or equal to 36.5 kW.

Step 6: Size Branch Feeders
For each panel, add the diversified loads served by that panel: Mechanical panel

20 units x 1 kW x 0.7 (diversity factor) = 14 kW


Lighting panel

44 units x 0.5 kW x 0.5 (diversity factor) = 11 kW

General receptacle panel:
8 units x 1.5 kW x 0.35 (diversity factor) = 4.2 kW Select branch feeder cables with current ratings greater than or equal to the sum of the diversified loads served by each panel. Flag for review