Question: Hello. I am trying to size main feeder and branch feeders for a 4 story military dorm. Here is the distribution. Main service on 1st floor servers 10 individual panels separated by mechanical, lighting and general receptacle loads. On the 2nd, 3rd and 4th floors, there are large distribution panels that serve the same for each floor. Where do I start with diversifying the load? There are approximately 8 dorm units served from each general receptacle panel, about 20 units served from the mechanical panel and 44 from the lighting panels. Approximately the same for each floor. I am having issues understanding how to apply the diversity. For the record, there is no fixed cooking equipment.
Step 1: Determine Base Load
Calculate the peak demand for each type of load (mechanical, lighting, general receptacle) based on the number of units served and their typical loads. For example: Mechanical load
20 units x 1 kW = 20 kW
Lighting load
44 units x 0.5 kW = 22 kW
General receptacle load
8 units x 1.5 kW = 12 kW
Step 2: Apply Diversity Factors Mechanical load
70% (typical diversity factor for mechanical loads)
Lighting load
50% (typical diversity factor for lighting loads)
General receptacle load
35% (typical diversity factor for receptacle loads)
Step 3: Calculate Diversified Load
Multiply the base load by the corresponding diversity factor: Diversified mechanical load
20 kW x 0.7 = 14 kW
Diversified lighting load
22 kW x 0.5 = 11 kW
Diversified general receptacle load
12 kW x 0.35 = 4.2 kW
Step 4: Determine Total Diversified Load
Sum the diversified loads for all three panels on each floor: 2nd, 3rd, and 4th Floors
14 kW (mechanical) + 11 kW (lighting) + 4.2 kW (general receptacle) =
29.2 kWStep 5: Size Main Feeder Multiply the total diversified load by the demand factor (typically 1.25 or 1.3): 29.2 kW x 1.25 = 36.5 kW Select a main feeder cable with a current rating greater than or equal to 36.5 kW.
Step 6: Size Branch Feeders For each panel, add the diversified loads served by that panel: Mechanical panel
20 units x 1 kW x 0.7 (diversity factor) = 14 kW
Lighting panel
44 units x 0.5 kW x 0.5 (diversity factor) = 11 kW
General receptacle panel: 8 units x 1.5 kW x 0.35 (diversity factor) = 4.2 kW Select branch feeder cables with current ratings greater than or equal to the sum of the diversified loads served by each panel. Flag for review