Topic: Emgergency Lighting Contactor

User: Michael Cotter, Location: Telford, Pa

Asked on: Friday, February 4, 2011 at 9:11 am EST
Answered on: Tuesday, May 14, 2024 at 1:08 am EDT

Question: The building I am investigating is a old system that has genertor feeding into a lighting contactor that supplies power to a emgergency lighting panelboard, all located in the generator room. A undervoltage relay tied into the normal power switchboard will start the generator and close the contactor. The emergency lights in the building are dedicated fixtures being supplied by the emergency lighting panelboard. My plan is to replace the generator and lighting contactor but do I need a lighting contactor listed for emgergency use, ie. UL 924?

Yes, if you are replacing the lighting contactor, it should be listed for emergency use, such as UL 924.

Reasons



National Electrical Code (NEC) Requirement

Emergency lighting systems must comply with NEC Article 700, which requires the use of emergency lighting equipment that is listed and labeled (see NEC 700.5(C)).


UL 924 Standard

UL 924 is a standard that establishes specific requirements for emergency lighting equipment, including lighting contactors. Contactors listed under this standard have been tested and evaluated to ensure they are suitable for use in emergency lighting systems.

Safety and Reliability

Emergency lighting contactors are designed to operate reliably in the event of a normal power failure. They are typically equipped with manual override features and have special coils that withstand sustained overloads during emergency operations.


Inspection and Approval:
Many authorities having jurisdiction (AHJs) require the use of listed emergency lighting equipment during inspections and approvals. Using a UL 924-listed lighting contactor helps ensure compliance with code requirements and avoids potential issues during inspections.Therefore, replacing the lighting contactor with a UL 924-listed model is recommended to ensure the safety and reliability of your emergency lighting system and to comply with applicable codes and standards. Flag for review