Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: 15KV Temp Feeders

User: Alwayslearningelec, Location: NJ

Asked on: Friday, February 4, 2011 at 9:14 am EST
Answered on: Tuesday, May 14, 2024 at 1:09 am EDT

Question: Install a temp 15kv feeder in 4" RGS w 3#2/0. it will be going 350' from an existing manhole( we need to do HV splicing because the existing feeder is being removed) to a new manhole were we will stub out 5'. Okay are there any disconnects required by code for this becuase the documents say to provide disconnects but I don't think this ONE run from mahole to manhole requires it.Thanks.

Yes, disconnects are required by code for this application.National Electrical Code (NEC) Requirements



NEC 490.11(A)(1)

Service overcurrent devices shall be located on the supply side of all other overcurrent devices.


NEC 490.11(D)

Where additional branch-circuit overcurrent devices are required for voltage drop or where the branch-circuit protective device does not provide the required ground-fault protection, the branch-circuit overcurrent protective device shall be connected on the load side of the service overcurrent protective device.

Application to Your Scenario

The temporary feeder is connected to an existing manhole, which is considered the "supply side." The feeder terminates at a new manhole, which is considered the "load side." The existing feeder is being removed, so the new feeder will be the only source of power to the new manhole. Therefore, a disconnect is required on the load side (at the new manhole) to meet the NEC requirements for service overcurrent protection.

Additional Considerations:
The disconnect should be rated for the maximum current draw of the load and should be readily accessible for servicing. If the feeder is encased in a transformer, the disconnect should be located outside the transformer enclosure.* If the feeder is underground, the disconnect should be located in a waterproof enclosure. Flag for review

Previous Question Next Question