User: steve66, Location: Illinois
Asked on: Friday, February 4, 2011 at 10:50 am EST
Answered on: Tuesday, May 14, 2024 at 1:09 am EDT
Question: I am trying to predict the amount of harmonic currents that will be present on the service to a building. I know the building will have a lot of personal computers, and a lot of electronic ballasts for fluorescent lights.I know the fluorescent ballasts have less than 10% THD, but I'm not sure about the computers. Also, I'm not sure how much of the 10% THD is in which harmonic. Is most of it in the 3rd harmonic? Or is it more spread out across the higher harmonics.If anyone has a reference that indicates what the harmoic distrortion vs. frequency is for lights and personal computers, I would appreciate it. For example, maybe something that says standard fluoresenct ballasts have X% at the 3rd harmonic, Y% at the 5th, and so on.I searched the internet, and haven't been able to find anything.Thanks:Steve
Harmonic Distortion from Electronic DevicesPersonal Computers Most modern personal computers have power supplies with low harmonic distortion (<5%). However, older computers and those with high-power components (e.g., gaming PCs) may have higher harmonic levels.
Electronic Ballasts for Fluorescent Lights Electronic ballasts typically have lower harmonic distortion than magnetic ballasts. Harmonic distortion levels vary depending on the ballast type and manufacturer.
Specific Harmonic Content
The harmonic content of electronic devices varies widely. However, some general trends can be observed: 3rd Harmonic
Usually one of the dominant harmonics for electronic devices.
5th Harmonic
Present but typically less significant than the 3rd.
Higher Harmonics
Amplitude decreases as harmonic order increases.
References IEEE Std 519-2014
Recommended Practice and Requirements for Harmonic Control in Electric Power Systems
EPRI Technical Report 1023775
Harmonics and Power System Equipment
UL 1012
Standard for Luminaires (includes harmonic distortion limits for electronic ballasts)
Approximation for Harmonic Distortion
As an approximation, you can assume the following harmonic distortion levels: Personal Computers
5% (primarily 3rd harmonic)
Electronic Ballasts
10% (approximately 70% in the 3rd harmonic, 20% in the 5th)
Estimating Harmonic Currents
To estimate the harmonic currents, you can use the following steps:1. Determine the total load current (amps) for the computers and lights.
2. Multiply the load current by the harmonic distortion percentage for each harmonic.3. Add the harmonic currents for each harmonic to get the total harmonic distortion (THD).
Example
Load current: 10 amps PC distortion: 5% (primarily 3rd harmonic) Ballast distortion: 10% (70% in the 3rd harmonic, 20% in the 5th)
3rd Harmonic Current
10 amps 0.05 0.7 = 0.35 amps
5th Harmonic Current
10 amps 0.1 * 0.2 = 0.2 amps
Total THD
0.35 amps + 0.2 amps = 0.55 amps (5.5%)
Note: This is just an approximation, and actual harmonic levels may vary depending on the specific devices and operating conditions. Flag for review