Topic: EGC in parallel runs

User: sbutler, Location: North Charleston, SC

Asked on: Friday, February 4, 2011 at 11:01 am EST
Answered on: Tuesday, May 14, 2024 at 1:09 am EDT

Question: Per 250.122(F), it requires the GEC to be sized per table 250.122 for each parallel run regardless of the feeder size. The contractor installed parallel (2 -runs) #350's with a #4 GEC connected to a 600A disconnect switch. By table 250.122 and 250.122(F), it looks like #1 is required in each run. Does anyone know if there is an exception that allows for a smaller GEC?Thanks for any and all replies.

There is not an exception that allows for a smaller GEC in this case. The GEC must be sized per Table 250.122 for each parallel run regardless of the feeder size. Therefore, the contractor should install #1 GECs for each of the two #350 parallel runs. Flag for review