User: Dennis Alwon, Location: Chapel Hill, NC
Asked on: Saturday, February 5, 2011 at 11:44 am EST
Answered on: Tuesday, May 14, 2024 at 1:11 am EDT
Question: I was reading an article in electrical contractor (Jan, 2011 edition). The Article is called Word of Mouth by Richard Bingham.I was curious about the bolded section. Any comments...There is one written item that really affects designing, installing and monitoring for the optimal quality of supply (which also means minimal power quality problems). It is Article 250.56, which reads, "Resistance of Rod, Pipe, and Plate electrodes. A single electrode consisting a rod, pipe, or plate that does not have resistance to ground of 25 ohms or less . all be augmented by one additional ode of any of the types specified by 250.52(A)(2) through (A)(7).? The 25-ohm number has been taken further by some organizations to state much lower numbers, including, "the installation manual of the ground must be less than 1 ohm the reference section." This is missing reason for the original requirement, which was not intended to improve the quality of the supply but rather to provide adequate low-impedance path for fault current to flow, which would allow for the overcurrent circuit protection (breakers fuses) to trip and clear the fault quickly.MIL- HDBK-419A and others indicate that 10 ohms is the maximum for adequate lightning protection, while the Institute of Electrical and Electronics Engineers (IEEE) Std. 141 (The Red Book) points to a 5-ohm recommendation.
The bolded section you mentioned highlights the differing opinions and recommendations regarding the resistance of grounding electrodes. While the National Electrical Code (NEC) specifies a limit of 25 ohms, some organizations suggest lower resistance values, including less than 1 ohm or 5 ohms, for optimal grounding effectiveness.The reason for the original 25-ohm requirement in the NEC was not primarily to improve the quality of the electrical supply but to ensure an adequate low-impedance path for fault current to flow. This ensures that overcurrent protection devices (circuit breakers or fuses) can trip quickly and clear a fault condition.However, for specific applications such as lightning protection, lower resistance values may be necessary. MIL-HDBK-419A suggests a maximum resistance of 10 ohms for adequate lightning protection, while IEEE Std. 141 recommends a 5-ohm limit.Ultimately, the appropriate resistance value for a grounding electrode depends on the specific application and the requirements of the applicable codes and standards. Electrical engineers and professionals should consider the purpose of the grounding system, the fault current levels, and any additional requirements for lightning protection or other factors when determining the suitable grounding electrode resistance. Flag for review