User: dconrad, Location: oregon
Asked on: Saturday, February 5, 2011 at 6:38 pm EST
Answered on: Tuesday, May 14, 2024 at 1:11 am EDT
Question: I have a breaker tripping and can't seem to figure out whats causing it. When ever we have a power outage, one breaker powering an out building trips, I will start @ the utility and walk you down stream to give the whole picture. Utility is 300 KVA MV-480/277 and is feed by 10 sets of 600MCM to a 4000A switchboard, we are then feeding a distribution panel with a 800 amp breaker. Out of this we are coming off a 125 amp breaker feeding a 75 KVA trans 480/208/120 feeding the load center in the building.The 125 amp breaker is the one tripping. Under full load it has 63.5 amps on A phase and 53.5 on B phase and about 8 amps on the neutral. What am I missing?
Possible Causes of Breaker Tripping
1. Overcurrent
Check the load connected to the 125-amp breaker. Ensure that it does not exceed the rated current of the breaker (125 amps). Use an ammeter to verify the current draw on each phase under full load. Your readings (63.5A, 53.5A, 8A) indicate a possible imbalance of load among the phases, which could contribute to overcurrent tripping.
2. Loose or Corroded Connections
Inspect all electrical connections, including those at the utility, distribution panel, transformer, and load center. Check for any loose wires, loose terminals, or signs of corrosion. Loose connections can create resistance and cause overheating, leading to breaker tripping.
3. Faulty Transformer
Verify that the 75 KVA transformer is not faulty. A faulty transformer can draw excessive current and cause breaker tripping. Check the transformer's insulation resistance and turns ratio to ensure proper operation.
4. Power Surges or Transients
Power outages can generate power surges or transients that can damage electrical components. Consider installing surge protectors to mitigate the effects of power surges.
5. Short Circuit
A short circuit occurs when a live wire comes into contact with a ground or another live wire. Inspect the load connected to the breaker for any damaged insulation, splices, or other potential short circuit points.
6. Defective Breaker
Although less likely, the 125-amp breaker itself may be defective. Consult with an electrician to test the breaker and replace it if necessary.
Steps to Troubleshoot
1.
Isolate the Load
Disconnect all loads from the breaker and reset it. If it holds, the fault is likely in the load. Reconnect the loads one by one to identify the faulty component.2.
Check Connections
Tighten all electrical connections and inspect for corrosion.3.
Test the Transformer
Use an insulation tester and turns ratio meter to check the transformer's condition.4.
Eliminate Transients
Install surge protectors at the load center and distribution panel.5.
Rule Out Short Circuits
Visually inspect the load for any visible damage or loose connections.6.
Consider a Breaker Fault: If all other possibilities are eliminated, consider the possibility of a defective breaker and consult an electrician. Flag for review