Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Supplementary equipment grounding conductor

User: smallfish, Location: Detroit

Asked on: Saturday, February 5, 2011 at 8:17 pm EST
Answered on: Tuesday, May 14, 2024 at 1:11 am EDT

Question: A length of twenty feet of EMT encloses only circuit conductors and is run on wooden supports across an outside roof to an AC unit. The roof space is narrow and the EMT is subject to physical damage and separation from being stepped on or tripped over by workmen.Does Section 250.96 (A) of the 2008 NEC with its reference to the "use of supplementary equipment grounding conductors" allow an electrical inspector to request that an equipment grounding conductor in the form of a wire be run with these circuit conductors?And if so, is it permitted to run this wire either on the inside or the outside of the EMT?Thanks

Yes, Section 250.96(A) of the 2008 NEC allows an electrical inspector to request an equipment grounding conductor wire be run with the circuit conductors in this situation.

Section 250.96(A) states that:> "Equipment grounding conductors and equipment-grounding bonding jumpers shall be installed in raceways, where used for branch circuits, feeders, or services, or within enclosures where installed under the provisions of 250.30(A)(1) and (A)(2). Equipment grounding conductors installed in raceways shall be run with the circuit conductors in the same raceway, with one exception: in the case of branch circuits where the equipment grounding conductor is not contained within the cable, the equipment grounding conductor shall be run with the circuit conductors."The wire can be run either on the inside or the outside of the EMT.

If run inside the EMT, the wire must be insulated or covered for protection against contact with the EMT.If run outside the EMT, the wire must be attached to the EMT at intervals not exceeding 6 feet and must be protected from physical damage in accordance with Section 300.4(A) of the NEC. Flag for review

Previous Question Next Question