User: sparky62298, Location: Milwaukee, WI
Asked on: Saturday, February 5, 2011 at 11:18 pm EST
Answered on: Tuesday, May 14, 2024 at 1:12 am EDT
Question: I own a 4 family unit that is in desparate need of a service upgrade. My plan is install 5 100A load centers (1 for each unit and 1 public panel for basement/stairway lights, furnace, washer/dryer, etc). A 5 position meter bank would be installed outside. The utility would supply 400 amps to the meter bank (120/240V, 3-wire, single phase). My question is what do I use to size the GEC and how large would it need to be? I'm not sure if I am to size it off of one panel or off of the 400A supplied by the utility.Full disclosure: I'm a commercial electrician and I don't deal with residential work often, so I'm not real familiar with the codes that may apply to this multi-family unit.Also, while I'm at it, can someone verify the 310.15(B)(6) applies to multi-family units (i.e. can I run #4AWG wire to each unit's individual 100A service panel)?Thanks in advance for your opinions and comments.
GEC Sizing
The Grounding Electrode Conductor (GEC) is sized based on the largest service entrance conductor size. In this case, the utility is supplying 400 amps, which corresponds to a 4/0 AWG conductor. Therefore, the GEC must be: 4/0 AWG bare copper (Table 250.102)310.15(B)(6) Applicability to Multi-Family Units
Yes, 310.15(B)(6) applies to multi-family units. This section allows the use of #4 AWG conductors for branch circuits rated 100 amperes or less that supply single-family dwellings or multi-family dwelling units where all of the following conditions are met: The dwelling unit is served by a single 100 ampere or less service disconnect. The branch circuit originates at the service disconnect. The distance from the disconnect to the nearest outlet is not more than 50 feet. The branch circuit is protected by a single overcurrent device rated 100 amperes or less.In your case, it appears that each unit will have its own 100A service panel, so 310.15(B)(6) would not apply.
Panel Sizing
Each unit's load center should be sized based on the calculated electrical load for that unit. The public panel can be sized based on the needs of the shared areas.
Additional Notes Please consult with your local authority having jurisdiction (AHJ) to confirm the specific code requirements and any applicable permits. It is recommended to have a qualified electrician perform the installation and inspections. Remember to consider the future electrical needs of the units and size the service upgrades accordingly. Flag for review