User: wyreman, Location: SF CA USA
Asked on: Sunday, February 6, 2011 at 4:59 pm EST
Answered on: Tuesday, May 14, 2024 at 1:13 am EDT
Question: Two year old 800Amp 480/277v main has opened randomly now twice.Facility is very lightly loaded at the time [weekend night].Normally has much more HVAC and pools loads when occupied.Opening main sends fire alarm notifier to director of operations and cops.Director sees no reason main should be off and resets. Just fine.Next day same thing, but he calls me before reseting.I went with him that night in my PPE and we opened it up and looked for arcing/discolor, measured temperature and voltage. Couldn't clamp amps on the buswork but I only clamped less than 50 amp of load mostly pool pumps.Engineer's dials showST: pickup is at max which is 8ST: time is min = INSTGF: pickup min 1GF: time min INSTWe have had problems with these new breakers giving nuisance tripping.We have another 1200AMP 12Kv cabinet that really likes the loads to come back in a certain order.I would love to be there quickly after cb opens to see if the thermal delay calls it an overload or a faulty load that just pulls the main before the subbreaker.Question is why only intermittently? Faulty motor comes only sporadically?There is a tester [and a qualified test person] who can plug in and read the digitrips report.In the short term, and I don't want to take the fire responsibility for this, isn't the theory that you can "crank up" the dial on the main and this way the fault [if there is on] will show on the sub breakers?Any insides?Digitrip RMS 310
Possible Causes
Intermittent fault on a load
A faulty motor or other load may intermittently draw excessive current, causing the main breaker to trip.
Loose connections
Loose connections within the main circuit or sub-circuits can create high resistance and heat, leading to breaker tripping.
Overloaded circuit
Even though the facility is lightly loaded, there may be an underlying issue causing an overload on the main circuit.
Circuit design issues
The circuit may be improperly designed, resulting in unbalanced loads or excessive voltage drop.
Breaker malfunction
The main breaker itself may be faulty, causing it to trip even without an actual overload.
Troubleshooting
Conduct load testing
Use an ammeter to measure the current on all sub-circuits to identify any excessive loads.
Inspect connections
Thoroughly inspect all electrical connections, including busbars, terminals, and wire insulation, for loose or damaged components.
Analyze breaker settings
Ensure that the breaker settings (ST and GF) are appropriate for the load and circuit design.
Perform a breaker test
Have a qualified technician use a breaker tester to diagnose any potential faults with the breaker.
Monitor the circuit after resetting
If the main breaker continues to trip intermittently, monitor the circuit and sub-circuits closely to determine the root cause.
Short-Term Mitigation
Resetting the breaker
While it is not advisable to increase the breaker settings without fully understanding the cause, resetting the breaker may be necessary to restore power.
Isolating loads
If a fault is suspected on a sub-circuit, temporarily isolate the suspect load to determine if it is causing the tripping.
Close monitoring
Monitor the circuit and sub-circuits closely after resetting to detect any recurring issues.
Long-Term Solution
Repair or replace faulty components
Identify and repair any loose connections, faulty loads, or circuit design issues.
Adjust breaker settings
If the breaker settings are inappropriate, adjust them accordingly to provide adequate protection while minimizing nuisance tripping.
Upgrade the electrical system: If the circuit is overloaded or has other design flaws, consider upgrading the electrical system to improve reliability and prevent future problems. Flag for review