User: sw_ross, Location: NoDak
Asked on: Monday, February 7, 2011 at 8:57 am EST
Answered on: Tuesday, May 14, 2024 at 1:14 am EDT
Question: This is just for confirmation of what I think I know. Please enlighten me if I'm wrong in my understanding of this topic.With a multi-wire branch circuit you have to use two separate breakers with a listed handle tie, 210.4(B), 240.15(B)1.My 2 questions are:1) Is it allowed to use a 2-pole breaker for a multi-wire Branch circuit (or 3-pole for a 3 phase mwbc)?2) Outside of this mwbc topic, any branch circuit that has line-to-line loads you have to use a 2-pole breaker with a common trip (two separate breakers with handle tie doesn't qualify)?I just want some clarification on this issue to make sure I'm not being unjustly critical on fellow workers.Thanks,Sky
1) Yes, it is allowed to use a 2-pole breaker for a multi-wire branch circuit (or a 3-pole breaker for a 3-phase MWBC). The NEC does not prohibit the use of a 2-pole breaker for this purpose.2) Outside of the MWBC topic, any branch circuit that has line-to-line loads requires a 2-pole breaker with a common trip (two separate breakers with a handle tie does not qualify). This is because the NEC requires that all ungrounded conductors of a circuit be opened simultaneously in the event of a fault. A 2-pole breaker with a common trip ensures that this happens. Flag for review