Question: I was approached by my mechanical engineer to consider re-size of the cable of a motor as they?re thinking of getting a new motor for this pump and the new motor will be 125HP, whereas the old motor is 75HP. Below are the specs I found from the existing MCC design:Motor Volt FLA Cable Cable Ampacity Upstream Breaker125HP 460V 182 1-3/C #350kcmil 350 400AF/225AT75HP 460V 109 1-3/C #4/0 260 150AF/150ATThe FLA is calculated FLA assuming 0.8PF and 0.8 Eff. Cable ampacity is based on NEC table 310.16 assuming temp. rating 90C.Before I suggest to my mechanical engineer to go with a 3/C #350kcmil cable system (as the case for other 125HP machines on the same existing MCC), I want to understand if it is possible to utilize the existing #4/0 size cable as I feel its ampacity seems to be able to adequately accommodate the new 125HP motor. It?ll make a huge cost difference if we have to re-size and install new cables.I?m not as familiar in the sizing of cables, so my questions here are: are we able to use the existing 75HP cable system to accommodate the new 125HP motor? Also, what was the basis of determining the size of the cables as you can see that for the existing 125HP motor, our #350kcmil provides some ampacity reserve. Pretty much I want to know what's the math/calculation behind the specs that as shown above.Thank you.
Can the existing #4/0 cable accommodate the new 125HP motor?
Yes, the existing #4/0 cable can accommodate the new 125HP motor. The cable ampacity of #4/0 is 260A, which is greater than the FLA (Full Load Amperage) of the new motor, which is 182A.
Basis of determining the size of the cables
The size of the cables is determined based on the following factors:
FLA of the motor
The cable must be able to carry the maximum current that the motor draws, which is the FLA.
Voltage of the system
The cable must be rated for the voltage of the system in which it will be used.
Ampacity of the cable
The ampacity of the cable is the maximum current that the cable can carry continuously without overheating.
Temperature rating of the cable
The temperature rating of the cable indicates the maximum temperature that the cable can withstand without being damaged.
Case of the existing 125HP motor
The #350kcmil cable was chosen because it provides some ampacity reserve. This means that the cable can carry more current than the FLA of the motor. This reserve capacity may be useful in case the motor's load increases in the future.
Conclusion:
The existing #4/0 cable can be used to accommodate the new 125HP motor. The cable ampacity is greater than the FLA of the motor, and it meets the other necessary requirements. Re-sizing the cable is not necessary, and it would result in significant cost savings. Flag for review