Question: Ok as an electrician I have always believed THHN wire could not be run in walls etc. Now I am being asked for a code reference stating THHN can not be run inside residential walls without protection. Can anyone point me to the proper place in the 2011 book?
2011 National Electrical Code (NEC)Article 334: Non-Metallic Sheathed CableSection 334.10(A)(1) states:> "Type THHN. For general use in dry locations as follows:>> ...>> Not in raceways or embedded in masonry, concrete, aggregate, or fill> Not in Class III locations" Flag for review