Topic: Receptacle Required Near A/C Condenser

User: David40, Location: Logan, Utah

Asked on: Monday, February 7, 2011 at 11:49 am EST
Answered on: Tuesday, May 14, 2024 at 1:14 am EDT

Question: I know we are required to install a receptacle near an A/C condenser. Is that part of the electrical code or the mechanical code? What is the Article / Section that applies.Thanks

National Electrical Code (NEC)Article 440: Air-Conditioning and Refrigeration EquipmentSection 440.22: Receptacles for Air-Conditioning and Refrigeration Equipment"Where ducts or plenums are located in attics or other spaces used for equipment other than duct work, a receptacle outlet shall be installed for servicing such equipment." Flag for review