User: Alwayslearningelec, Location: NJ
Asked on: Monday, February 7, 2011 at 1:15 pm EST
Answered on: Tuesday, May 14, 2024 at 1:15 am EDT
Question: If you have 120/208 v panel with (1) 20a ckt feeding three different areas of lights(all off the same ONE ckt) and they are 75', 150 and 250' away. We will run MC for these to as close as possible to the panel. I am coming up that #6 wire is needed for the fixtures furthest away. This does not seem right. Thanks.
Your concern is valid. #6 wire for a 20A circuit at 250' does not seem appropriate.Let's check your calculations
Step 1: Determine the Load
Three areas of lights are connected to the same 20A circuit, so the total load is the sum of the loads in each area.
Step 2: Calculate the Voltage Drop For a 120/208V panel, the maximum voltage drop allowed is 5% of 120V, which is 6V. The voltage drop formula: V = I R L Where: V = voltage drop, I = current, R = resistance, L = lengthStep 3: Determine the Resistance
For multi-conductor cables like MC, the resistance per foot can be found in the product specifications.
Step 4: Calculate the Length
You have 75', 150', and 250' runs. For each run, you need to calculate the total length from the panel to the fixture.
Step 5: Check the Voltage Drop
Once you have the resistance and the length, you can calculate the voltage drop for each run.
Example Calculation for the 250' Run
Assuming the resistance is 0.005 ohms per foot for 3 conductors Total length: 250' 2 (to and from panel) = 500' Voltage drop: V = 20A 0.005 ohms/ft * 500ft = 5V
Based on these calculations, #6 wire would be sufficient for all three runs. #6 wire has a resistance of approximately 0.005 ohms per foot, and the voltage drop for all three runs is less than 5%.
Therefore, your concern about using #6 wire for the 250' run is not valid. Please double-check your calculations or provide more details about the specific MC cable you plan to use. Flag for review