Topic: 408.4 (B) Source of Supply

User: tom baker, Location: Bremerton, Washington

Asked on: Monday, February 7, 2011 at 5:29 pm EST
Answered on: Tuesday, May 14, 2024 at 1:16 am EDT

Question: This new rule requires the source of supply to be marked on switchboards and panelboards.But the rules does not apply to fused switches, which are in Art 404. Was that an oversight or intentional?Considering a code proposal.

IntentionalFused switches are not classified as switchboards or panelboards, and therefore, the marking requirement would not apply to them. Flag for review