Topic: Does Table Annex C have correct fill for THHW, THW, and THW-2 sizes 14, 12, 10 and 8?

User: nercGerald, Location: San Jose, CA

Asked on: Monday, February 7, 2011 at 9:00 pm EST
Answered on: Tuesday, May 14, 2024 at 1:17 am EDT

Question: It looks like these wire sizes and insulations should have the same fill as TW since they have the same cross sectional areas as TW. But they are grouped with RHH*, RHW*, and RHW-2* in Tables C.1, C.2, C.3, C.4, C.5, C.6, C.7, C.8, C.9. C.10, C.11, C.12.

You are correct that the fill of these wire sizes and insulations should be the same as TW since they have the same cross sectional areas. However, they are grouped with RHH, RHW, and RHW-2 in Tables C.1, C.2, C.3, C.4, C.5, C.6, C.7, C.8, C.9. C.10, C.11, C.12 because they have different temperature ratings. TW is rated for 60°C, while RHH, RHW, and RHW-2 are rated for 75°C, 90°C, and 90°C, respectively. Flag for review