User: Howard Burger, Location: N of Anchrage, AK
Asked on: Monday, February 7, 2011 at 9:07 pm EST
Answered on: Tuesday, May 14, 2024 at 1:17 am EDT
Question: New construction, major grocery chain. Commercial meat grinder, 8.5hp, comes with L15-30 plug on #8 awg SO cord. We're going to run an SO cord with connector from fused disconnect to the provided cord plug so that the unit can be disconnected and moved for cleaning.I figure OCPD size to be 67.1 amps, max. The panel schedule calls for 50/3 breaker.Lead journeyman says can't have 30 amp cord plug on 50 amp breaker (thinking possibly of 210.21.B.1?); my thought was that the cap is OK because the 50 amp breaker is for startup current, and the wire is protected by the fused disconnect, which I figured should be 37.5 amps (data plate shows 30 amps).Should we put a bigger plug on the cord? To add confusion to the issue, the plans call for #10 wires from the panel.(My amps figures comes from extrapolataing T450.250 since it jumps from 7.5hp to 10 hp; I got 26.84 for the amperage for an 8.5hp motor.)
Determining OCPD Size
According to the data plate, the motor draws 30 amps. Applying the motor current calculation (26.84 amps for 8.5hp from NEC Table 430.250) is not recommended, as it does not account for all factors (e.g., starting current). The OCPD size should be 30 amps, as per the data plate.
Cord Plug and Breaker Size
The motor data plate specifies a 30-amp fuse. According to NEC 430.113(B), the cord plug ampacity should match the OCPD ampacity. Therefore, a 30-amp cord plug should be used.
Panel Schedule and Wire Size
The panel schedule calling for a 50/3 breaker is incorrect. The OCPD size should be 30 amps for a 30-amp motor. The plans calling for #10 wires are also incorrect. #8 wires are required for a 30-amp circuit, per NEC Table 310.15(B)(16).
Fused Disconnect
A fused disconnect is required for cord-and-plug connected motors to provide a convenient means of disconnecting the motor from the electrical supply. The fused disconnect should have a fuse ampacity of 30 amps, matching the motor data plate and the OCPD size.
Conclusion:
The correct setup is: 30-amp OCPD (breaker) 30-amp fused disconnect #8 SO cord with L15-30 plug #8 wires from the panelThe lead journeyman's concern about using a 30-amp cord plug on a 50-amp breaker is unfounded. The 50-amp breaker is for protecting the wires during motor startup, while the fused disconnect protects the cord. Flag for review