Topic: Panel Board Enclosure Used for Bonding

User: Ddexter, Location: Logan, Utah

Asked on: Monday, February 7, 2011 at 10:55 pm EST
Answered on: Tuesday, May 14, 2024 at 1:17 am EDT

Question: Here is a question for all who would like to respond.The enclosure for a panel board has a 3" conduit entering the bottom without a suplimental equipment ground installed. The ground terminal bar is located on the panelboard which is adjusted out from the back of the enclosure to flush up with the cover. The conduit is being use as an equipment ground. Would the enclosure infact be used here as a equipment bonding jumper???Is the enclosure listed and or labled for this application and for the sake of argument we could use lets say a GE enclosure or any enclosure for that matter????The panel board instruction say to bond the equipment terminal bar to the enclosure and to terminate all equipment grounds to the terminal bar provided.

Enclosure as Equipment Bonding Jumper

Yes, in this case, the enclosure can be used as an equipment bonding jumper. When the conduit entering the enclosure is used as the equipment grounding conductor, the enclosure becomes part of the equipment grounding path. The enclosure provides a continuous electrical connection between the panelboard and the equipment connected to the conduit.

Listing and Labeling

Enclosures are typically not listed or labeled specifically for use as equipment bonding jumpers. However, the National Electrical Code (NEC) allows the use of enclosures as equipment bonding jumpers if they meet certain requirements: The enclosure must be of conductive material, such as metal or non-metallic with a conductive coating. The enclosure must be bonded to the equipment grounding conductor or terminal bar using a suitable bonding jumper. The enclosure must be securely fastened to the panelboard.

NEC Requirements

The NEC requires that all panelboard enclosures be grounded. This can be done through a variety of methods, including:
Connecting an equipment grounding conductor to the terminal bar in the panelboard and bonding the terminal bar to the enclosure. Using the conduit as the equipment grounding conductor and bonding the conduit to the enclosure. Using an external equipment grounding conductor to connect the panelboard enclosure to the main grounding electrode system.

Conclusion

In the provided scenario, where a 3" conduit is entering the bottom of a panelboard enclosure without a supplemental equipment ground, the enclosure can be used as an equipment bonding jumper if the following conditions are met: The enclosure is conductive and meets the requirements of the NEC. The conduit is bonded to the equipment grounding terminal bar in the panelboard.* The panelboard is appropriately grounded. Flag for review