User: DOA_Kilovolt, Location: Upstate NY
Asked on: Tuesday, February 8, 2011 at 1:36 am EST
Answered on: Tuesday, May 14, 2024 at 1:17 am EDT
Question: I have multiple sets of #4 THHN that terminates on 20A breakers. The max size conductor allowed on breaker terminal is #8. The wire is upsized to allow for #CCC (16 ) in EMT and VD (1%). Installation is for PV system using micro-inverters. Is it permissible to splice to #12 for termination to breaker ?
No, it is not permissible to splice #4 THHN to #12 THHN for termination to a 20A breaker.Reasons
Code Violation
NEC Article 310.15(B)(16) prohibits splices or taps in conductors larger than #10 AWG intended for connection to terminals of devices rated 60A or less.
Safety Hazard
A poorly executed splice can increase resistance and create a potential fire hazard.
Increased Voltage Drop
Reducing the conductor size will increase the voltage drop, which can affect the performance and lifespan of the PV system.
Overheating
The #12 conductors may overheat under the load of #4 conductors, leading to premature failure.
Correct Approach: Use a breaker rated for #4 THHN wire, such as a 40A breaker. Terminate the #4 THHN wires directly to the breaker terminals without splicing.* Alternatively, consider using a subpanel with breakers sized appropriately for the #4 THHN wire. Flag for review