Question: I have a 120 / 208 panel fed by a 45 kva trans that supplys power to plc's , meters and other low voltage equipment by about six cb's from this panel . Should this trans short out all their process would come to a halt until power is restored and time would be a critical factor.Is there a quick method to resupply power to the panel ? Would a second trans wired to a double throw switch to be able to switch each load side of trans to the panel be code complient ? Each trans will have its own primary cb.Any other ideas ?Other circuits are also in this panel but are not critical. There is no other source of 120volts within atleast 300'.
Method 1: Double Throw Switch Install a double throw switch between the primary breakers of the two transformers. Connect the load side of each transformer to the appropriate side of the switch. In case of a transformer failure, switch the load to the secondary transformer.
Code Compliance
This method is code compliant if the switch is rated for the maximum current of both transformers combined. The switch should be installed in a readily accessible location. The switch should be clearly labeled to indicate the purpose and operation.
Other Ideas
Redundant Transformers
Install two separate transformers rated for the full load and connect them in parallel. This provides a backup transformer in case of a failure.
Secondary Circuit Switchgear
Install a secondary circuit breaker or fuse panel for each critical circuit. This allows for isolating and repairing individual circuits without affecting the rest of the panel.
Automatic Transfer Switch (ATS)
Install an ATS that monitors the primary power supply and automatically switches to a secondary source (e.g., a standby generator) in case of a failure.
Additional Considerations: Ensure that the secondary transformers are properly sized for the load. Provide adequate ventilation and cooling for the transformers. Consider installing surge protection devices to protect the transformers and equipment from transient voltage surges.* Establish clear emergency response procedures for power outages. Flag for review