Question: Is a seal required when conduit goes from one class 2, div 2 area to another class 2div 2 area? Code does not seem real clear.Is seal required with the conduit extending up from a dust-ignition proof enclosure20' and into an unclassified area?
Conduit between Class 2, Div 2 Areas
NEC 501.10(D)(1) does not require sealing when conduit penetrates a boundary between Class 2, Div 2 areas.
Conduit from Dust-Ignition Proof Enclosure to Unclassified Area:
NEC 500.8(D) requires sealing where a conduit extends from a dust-ignition proof enclosure into an unclassified area, regardless of whether the enclosure is in a hazardous area. This is to prevent the propagation of dust from the enclosure into the unclassified area. Flag for review