User: DBURBS, Location: Ohio
Asked on: Tuesday, February 8, 2011 at 3:06 pm EST
Answered on: Tuesday, May 14, 2024 at 1:18 am EDT
Question: I have a 800 amp service in a mall that needs to be split into a 600 and a 200 amp , can I tap the load side of the 800 amp FDS with parallel #2 conductors 40 feet long
No, you cannot tap the load side of the 800-amp FDS with parallel #2 conductors 40 feet long to split it into a 600-amp and a 200-amp service.The National Electrical Code (NEC) does not allow tapping the load side of a fused disconnect switch (FDS) for service. FDSs are designed to provide overcurrent protection for the feeder conductors, and tapping the load side defeats this purpose.Additionally, the length of the parallel conductors (40 feet) is too long for #2 conductors to safely carry the required current. The NEC limits the length of parallel conductors to 25 feet for #2 conductors carrying 100% of their ampacity.To properly split the 800-amp service, you should use a main breaker panelboard or switchboard with the appropriate number and size of circuit breakers or fuses. Flag for review