User: h1h2h3, Location: MA
Asked on: Tuesday, February 8, 2011 at 3:30 pm EST
Answered on: Tuesday, May 14, 2024 at 1:18 am EDT
Question: I am on a job where we have a group of existing heat pumps that need to be checked for proper installation. The manufacturers name plate states that the maximum time delay fuse or HACR C/B allowed is 15A, however, upon opening the discos we found that they were fused with 20A time delay fuses. It is my understanding that, ideally, the disco should be fused in accordance with the pumps FLA and should not exceed the maximum fuse allowed by the manufacturer. Our plan was to swap out all the 20A fuses with new 15A fuses, and all the 30A fuses with 25A fuses (there are several heat pumps with max allowable fusing at 25A). Does anyone see where this might be an issue? Are we correct in assuming that they should be changed? Motors and HVAC are not my strong suit and i would appreciate any feed back.Also, FYI, the branch circuit is sized correctly and is protected up to the disco accordingly, that is 20A C/B for #12 and 30A C/B for #10. Also, the units have no integral fuses or OL protection that we can see.Thank you again.God bless.
Yes, you are correct in assuming that the fuses should be changed to match the maximum fuse allowed by the manufacturer.Reasons
Overcurrent protection
Fuses protect the equipment from damage due to excessive current flow. Using fuses that exceed the manufacturer's rating could result in the fuses not tripping when there is a fault, potentially leading to overheating and damage.
Code compliance
The National Electrical Code (NEC) requires that overcurrent protection devices be rated at or less than the maximum fuse rating specified by the equipment manufacturer.
Manufacturer's warranty
Using fuses that exceed the manufacturer's rating may void the equipment's warranty.
Regarding the swap out
15A fuses for 20A discos
Correct. Swap out all 20A fuses with 15A fuses.
25A fuses for 30A discos
Correct. Swap out all 30A fuses with 25A fuses.
Additional considerations
Verify the FLA
Ensure that the FLA of the heat pumps is within the allowable range of the new fuses.
In-line fuses
If there are any in-line fuses between the disco and the heat pump, ensure that they are rated appropriately.
Heat pump age and condition
Older heat pumps may have degraded and may require lower FLA fuses.
Note: Always consult with an electrician or qualified HVAC technician if you are unsure about any electrical work. Flag for review