User: VIC1958, Location: Massachusetts
Asked on: Tuesday, February 8, 2011 at 5:44 pm EST
Answered on: Tuesday, May 14, 2024 at 1:19 am EDT
Question: I have a 11' long bathromm countertop with 3 individual drop-in sinks. I have a GFI on each end of the counter top to service the 2 outer sinks, do I need to add an additional GFI in the center to service the middle sink? The middle sink is over 3' from the edge of the sink to the 2 outer GFI's. This set up is in a commercial building.Thanks
Yes, you need to add an additional GFI in the center to service the middle sink.According to the National Electrical Code (NEC): GFCIs (Ground Fault Circuit Interrupters) are required for all 120-volt, single-phase, 15- and 20-ampere receptacles installed in bathrooms (and other wet locations). GFCIs must be listed as having "Class A" protection.* GFCIs must be located within 3' of the edge of the sink basin for sinks that are not supplied by a dedicated circuit.Since the middle sink is over 3' from the edge of the sink to the 2 outer GFI's, it is not serviced by the existing GFCIs. Therefore, an additional GFI must be added in the center. Flag for review