Question: I would appreciate any guidance on this matter... I am going to be doing a project where as I have to wire 5 smoke detectors together (2 in a front common hall, 2 in a rear common hall, one in the basement). The walls are concrete.Therefore, I was going to use either wire mold or emt as a raceway, and strip the sheathing off the romex at the locations where it will be inside the raceway. At either end I would have only about 1 inch of sheating entering the raceways. If I use emt, I would have a transition at either end to secure the romex. If I use wire mold, I would essentially do the same thing. Thus the raceway is simply that, a raceway and the 'cable' of romex is reduced to four conductors (hot, neutral, ground and red wire is signal wire) in a raceway.I am being told by a wiring inspector that this is a code violation because the wires are not THHN.Where does it state than romex wires are not THHN, and this method cannot be used?
NEC Code References
Article 334.10(3): "Electrical metallic tubing (EMT) shall be permitted to contain only the conductors of a single circuit." Article 336.12(B): "Wireways shall not contain conductors of different systems, voltages, or circuits unless separated by suitable barriers." Article 400.8(4): "NM cables shall be permitted to be installed in raceways. Where NM cable is installed in a raceway, the ampacity of the conductors shall be in accordance with Table 310.16."Interpretation
EMT is not permitted to contain the conductors of multiple circuits. Wireways (like wire mold) are not permitted to contain conductors of different circuits unless separated by barriers. NM cable is permitted to be installed in raceways, but the ampacity of the conductors must be reduced in accordance with Table 310.16.
Applicability to Your Project
In your case, you are attempting to wire 5 smoke detectors together using either EMT or wire mold. Each smoke detector would require its own circuit, so this would result in multiple circuits being installed in the same raceway, which is not permitted by the NEC.
Acceptable Solutions
To comply with the NEC, you could use the following methods:
Run separate EMT conduits for each circuit. This would involve running multiple EMT conduits from the panel to each smoke detector location. Use a larger raceway, such as wireway, and separate the circuits with barriers. This would involve using a wireway that is large enough to accommodate the conductors of all the circuits, and installing barriers to separate the circuits.* Use THHN wire inside the raceway. THHN wire is a type of wire that is specifically designed for use in raceways. It is rated for higher temperatures than NM cable, which allows for the full ampacity of the conductors to be used.
Conclusion:
The requirement for THHN wire in this case is based on the NEC code article that requires conductors in raceways to be rated for the temperatures present. Since NM cable is not rated for the temperatures present in EMT or wire mold, THHN wire must be used instead. Flag for review