Question: Ive been asked to do a build out for a machine shop. The building has a 3ph 480v wye system. Since most of the equipment is 3ph 230v, so the electrical engineer designed the job with a 480v to 230v transformer (delta to delta). Does this system need to be grounded? If so, how can I do that without an xo terminal? As of right now I have everything bonded throughout. Thanks
Yes, the system needs to be grounded.
Since the transformer is delta to delta, there is no neutral point for grounding. Therefore, you need to establish a grounding electrode system (GES) and connect it to the transformer's frame.
Grounding Method
Option 1: Grounding Rods Install a minimum of three grounding rods (8 feet or longer) at least 6 feet apart, driven into the earth. Connect the grounding rods together using solid copper wire (minimum #4 AWG). Connect the grounding electrode conductor (GEC) from the transformer's frame to the grounding rod system using the same wire size as the grounding rods.
Option 2: Buried Conductor Bury a bare copper conductor (minimum #4 AWG) at least 24 inches below grade and at least 6 feet away from any building or structure. Form a loop or oval with the buried conductor. Connect the GEC from the transformer's frame to the buried conductor using a junction box or by direct burial.
Option 3: Concrete-Encased Electrode Install a minimum of 20 feet of bare copper conductor (minimum #4 AWG) in concrete. The electrode should be at least 2 inches in diameter and encased in a minimum of 2 inches of concrete. Connect the GEC from the transformer's frame to the concrete-encased electrode using a junction box or by direct burial.
Additional Grounding Requirements
Bond all metal conduits, enclosures, and equipment to the GES. Install equipment grounding conductors (EGCs) for all equipment. Ensure that all ground connections are tight and have low resistance.
Note: The specific grounding method and requirements may vary depending on local building codes and electrical standards. It's essential to consult with a qualified electrician or electrical engineer for proper design and installation. Flag for review