Topic: Class 2 Division 2 Group G Light fixtures

User: electric85, Location: Mission Viejo, CA

Asked on: Tuesday, February 8, 2011 at 6:37 pm EST
Answered on: Tuesday, May 14, 2024 at 1:19 am EDT

Question: Does 502.130(B)2 allow the use of a dust tight light fixture that is not specifically rated class 2 division 2 as long as it complies with 500.8 (D)2? or does 500.8 (B)1 require it to be listed for the location?

  1. 130(B)2 allows the use of a dust-tight light fixture that is not specifically rated Class 2 Division 2 as long as it complies with 500.8(D)2.
    500.8(B)1 does not require it to be listed for the location.