Topic: using three wire for branch cicuits

User: tmason, Location: Fl

Asked on: Tuesday, February 8, 2011 at 6:42 pm EST
Answered on: Tuesday, May 14, 2024 at 1:19 am EDT

Question: im a new jersy electrictian i have a question concerning a 14-3 wire that was previously used as two circuits in a panel that i changed. i needed room in the paniel so i took a 14-3 circuit that i ohm out the black had 5 amps and the red had 4 i twited the two wires togeather and put one tail to a single 15 amp breaker is that legal or is it not im be told that you cant do that because its a inbalenced load could some one please help me and if you could verse and chapter would be great

Is it legal to combine two 14-3 wires to create a single 15-amp circuit?No, it is not legal.Rationale

Combining two 14-3 wires violates the following National Electrical Code (NEC) requirements:

Section 210.4(B)

A conductor shall not have its ampacity derated because of adjacent conductors in the same raceway or enclosure unless the derating factors specified in Section 310.15(B)(3)(a) are applied.


Section 310.15(B)(3)(a)

Where conductors of different sizes are installed together, the ampacity of each conductor shall be reduced in accordance with the derating factors given in Table 310.15(B)(3)(a).

Consequences of Combining Wires



Overheating and Fire Hazard

The combined wires will carry more current than their ampacity, which can lead to overheating and a fire hazard.


Imbalanced Load

The two wires will carry unequal currents, creating an imbalanced load that can put stress on the electrical system. This can lead to voltage fluctuations and other problems.

Code Violations

Combining wires in this manner violates the NEC and can result in failed inspections and potential legal issues.

Correct的做法:


The correct solution is to:
Remove the 14-3 wire from the panel. Install separate 14-2 wires for each circuit. Follow the NEC requirements for wire sizing and installation. Flag for review