User: RUMBA123, Location: Savannah, Ga.
Asked on: Tuesday, February 8, 2011 at 6:53 pm EST
Answered on: Tuesday, May 14, 2024 at 1:20 am EDT
Question: We are running 3 parallel 350 conductors in a single cable tray. The conductors are ran side by side with the first conductor being phase "A" the second phase "B" the third phase "C" and the fourth ground. The next conductor is phase "A" etc for 3 sets of conductors. An inspector, not the AHJ, is stating that the conductors are not grouped according to 392.8(D). All of the conductors are strapped down.What do you think?
According to NEC 392.8(D) conductors grouped together in a single raceway or enclosure shall be grouped according to their use or size. In this case, the conductors are grouped according to their use. The three phases are grouped together and the ground is grouped together. This grouping meets the requirements of 392.8(D).The inspector's interpretation of the code is incorrect. The conductors are properly grouped according to their use and the installation meets the requirements of the NEC. Flag for review