Topic: derating question

User: justinaway1, Location: West Coast

Asked on: Tuesday, February 8, 2011 at 7:24 pm EST
Answered on: Tuesday, May 14, 2024 at 1:20 am EDT

Question: How does table 310.15 B 2 apply if the loads are minimal; 4000 wiremold with 12dedicated 120v 20 amp receps? These are fed with #12 thhn.None of the loads will reach 9 amps. Am I in compliance? If not how do I remedy? Do Ineed to label unused outlets to let others know not to exceed derated value?

Compliance with Table 310.15(B)(2)

Table 310.15(B)(2) applies to wiring devices installed in hollow spaces, including underfloor raceways. It requires that the maximum allowable load be reduced by 20% for each additional outlet (receptacle) installed in a single outlet box.

Application to Your Situation

In your case, you have 4000 wire mold (raceway) with 12 dedicated 120V 20A receptacles. None of the loads will reach 9 amps.Since Table 310.15(B)(2) applies to wiring devices in hollow spaces, and wiremold is not considered a hollow space, this rule does not directly apply to your situation.

Nevertheless, it is still important to consider the potential for overloading

While the expected load may be below 9 amps for each receptacle, it is possible that multiple receptacles could be used simultaneously, resulting in a higher load. The #12 THHN wire used to feed the receptacles is rated for 20 amps, but the receptacles themselves are rated for 15 amps.

Recommendations

To ensure safety and compliance, consider the following recommendations:

Label Unused Outlets

Place labels on any unused outlets to indicate that they are not to be used. This will prevent others from inadvertently plugging in additional loads.


Derate Load

If the potential for overloading is a concern, consider derating the load on each receptacle to a lower value, such as 12 amps. This can be done by installing a different type of receptacle (e.g., 15A GFCI) or using a load balancer.*

Use Proper Wiring:
Ensure that the #12 THHN wire used to feed the receptacles is protected by an overcurrent device rated at 15 amps or less, to match the rating of the receptacles.By following these recommendations, you can help ensure the safe and reliable operation of your electrical system. Flag for review