User: 0308wayne, Location: iowa
Asked on: Tuesday, February 8, 2011 at 9:43 pm EST
Answered on: Tuesday, May 14, 2024 at 1:20 am EDT
Question: are afci breakers required on a residential branch circuit that supplies lighting outlets only? art. 100 has two definitions, outlet and lighting outlet, and 210.12B specifies outlets
No, AFCI breakers are not required on a residential branch circuit that supplies lighting outlets only.
Definition of Outlet Outlet
A point on the wiring system at which current is taken to supply utilization equipment. (Article 100)
Definition of Lighting Outlet Lighting Outlet
An outlet intended for the direct connection of a lampholder, a luminaire, or a lighting assembly. (Article 100)
Requirement for AFCI Breakers 210.12(B)
All 15- and 20-ampere, 120-volt, single-phase branch circuits supplying outlets or devices in dwelling units shall be protected by a listed arc-fault circuit interrupter (AFCI).
Interpretation
The requirement for AFCI breakers applies to outlets, not lighting outlets specifically. Since lighting outlets are a type of outlet, they would typically be included under the requirement for AFCI breakers.
Exception
However, there is an exception to the requirement for AFCI breakers on lighting outlets: 210.12(B) Exception: Branch circuits that supply only lighting outlets shall not be required to be protected by AFCIs.Therefore, AFCI breakers are not required on a residential branch circuit that supplies lighting outlets only. Flag for review