Topic: Loop system in NEC

User: skyline77, Location: Illinois

Asked on: Wednesday, February 9, 2011 at 5:08 am EST
Answered on: Tuesday, May 14, 2024 at 1:21 am EDT

Question: Hi,I would like to know if there is a loop system requirement in the NEC for healthcare facilities.

Yes, there is a loop system requirement in the NEC for healthcare facilities. It is located in Article 700 of the NEC.700.15(D) Loop System.

Where public address or emergency voice/alarm communication systems are required, one of the following systems shall be included:(1) A loop system shall be provided in each required wheelchair space when in the assembly area of a room or space and, in addition, shall be provided in at least 5 percent of all other fixed seating in each assembly area.(2) A system shall be provided that generates and transmits signals compatible with audio-frequency induction loops in such a manner that listeners using hearing aids equipped with induction coils or other assistive listening devices can listen to the proceedings or alerts. Such systems shall also comply with the requirements for "public address" or "emergency voice/alarm communication" systems as applicable.

Exception

A loop system shall not be required in assembly areas that will not contain fixed seating, in detention or correctional facilities, or in occupancies of Group I-1 or I-2.

Informational Note: For additional information, see NFPA 72,


National Fire Alarm and Signaling Code. Flag for review