Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: generator system for existing facility

User: Michael Hayes, Location: Miami Fla.

Asked on: Wednesday, February 9, 2011 at 10:51 am EST
Answered on: Tuesday, May 14, 2024 at 1:21 am EDT

Question: we are installing a new exterior generator and exterior ats for an existing facility. both to be located across the parking lot adjacent to the existing exterior pad mount transformer. the ats is service rated, 3-wire, solid neutral. the existing undergorund feeders from the transformer (which we will now flop into the ats) to existing building main electrical panel do not contain a grounding conductor. The electrical inspector is going to require us to now install grounding conductors in with these existing underground feeders. Is there any exception for existing situations so we dont have to install the grounding conductors?

NEC Exception 250.118(4)

This exception allows existing underground feeders without grounding conductors to be used with a separately derived system, such as a generator. However, the exception has the following conditions: The existing feeders must be in good condition. The system must be electrically isolated from all other systems. The generator and ATS must be listed for use with the existing feeders.

Steps to Comply with the Exception

Verify that the existing feeders are in good condition (e.g., no damaged insulation or corrosion). Ensure that the generator and ATS are listed for use with feeders without a grounding conductor. Provide documentation to the electrical inspector that the conditions of the exception are met.

Additional Considerations:
The electrical inspector may still require additional measures to ensure the safety of the installation, such as bonding the generator frame to the ATS. It is recommended to consult with a qualified electrician or engineer to ensure full compliance with all electrical codes and standards. Flag for review

Previous Question Next Question