Question: my formin is telling me that it is a code violation to put two 120 volt circuits in a two gang box with out a divider or means to turn both power sources off at the same time as far as i know you only need a divider when using two different voltages i put two gfi recepticles in a two gang box under a jacuzzi tub one 120 volt 15 amp for a hater motor and 120volt 20 for the pump motor is this against code in nj my look at this is that set up is no different then a two gang on a counter in a kitchen that has a 20 amp outlet and 15 amp switch for sink lite their is no devider needed would any one know somthing that i have missed if so please let me know
National Electrical Code (NEC)
According to the NEC, Article 314.28, "Where two or more circuits are installed in a box, they shall be separated by a permanent barrier." This applies to circuits of different voltages as well as circuits of the same voltage.
New Jersey Electrical Code (NECJ)
The NECJ has adopted the NEC in its entirety, including Article 314.28. Therefore, the requirement for a divider applies in New Jersey.
Your Situation
In your case, you have two 120-volt circuits in a two-gang box without a divider. This is a violation of the NEC and NECJ.
Reason for the Requirement
The requirement for a divider is to prevent accidental contact between energized parts of different circuits. This is especially important in cases where the circuits are being used to power equipment that is in close proximity to water, such as a jacuzzi tub.
Solution
To comply with the code, you need to install a divider in the two-gang box. This can be a metal or plastic barrier that separates the two circuits. You may also need to install a double-pole circuit breaker or switch that can turn off both circuits at the same time.
Conclusion
Your installation is in violation of the NEC and NECJ. To correct the violation, you need to install a divider and ensure that you have a double-pole circuit breaker or switch that can turn off both circuits simultaneously. Flag for review