Topic: Revision to UL676 - Standard for Underwater Luminaires

User: bphgravity, Location: Florida

Asked on: Wednesday, February 9, 2011 at 2:00 pm EST
Answered on: Tuesday, May 14, 2024 at 1:22 am EDT

Question: Hello Everyone,An important change has been made to UL676 Standard for Underwater Luminaires. In short, the term ?salt water? will be changed to ?sea water? in reference to product markings and when determining suitability of use for underwater luminaires. The change also stipulates that pools treated with salt for chlorine generation are still considered fresh water.Inspectors across the nation have not been approving underwater luminaires marked for ?fresh water? when used in salt water pools and have required luminaires marked for ?salt water? when chlorine generators are to be installed. This change should eliminate this issue. The electrical resistivity of salt water pools are well within the thresholds of ?fresh water? luminaires. Only true ?sea water? has a salt content and electrical resistivity to warrant the specially marked luminaire.For reference, water with a resistivity of 89 ohm-cm or higher (6000 ppm or less) is FRESH WATER. Water with a resistivity of 22 ohm-cm as found in the open sea and in therapeutic pools and spas is SEA WATER.Also be aware that many manufacturers test and list their products for both locations and are marked as such.

Notice Regarding UL676 Standard for Underwater LuminairesKey Points

The term "salt water" will be replaced with "sea water" in product markings and suitability determinations. Pools treated with salt for chlorine generation are still considered fresh water.

Background

Inspectors have been rejecting underwater luminaires marked for "fresh water" in salt water pools and requiring luminaires marked for "salt water" when chlorine generators are installed.

Clarification

The change in the UL676 Standard clarifies that: Water with a resistivity of 89 ohm-cm or higher (6000 ppm or less) is considered

FRESH WATER
. Water with a resistivity of 22 ohm-cm (as found in the open sea and therapeutic pools/spas) is considered SEA WATER.

Implications

The electrical resistivity of salt water pools is typically within the range of fresh water. Only luminaires specifically marked for "sea water" are necessary for use in the open sea or pools with high salt content.

Note:
* Some manufacturers list their products for both fresh and sea water use. Flag for review