User: sfav8r, Location: San Francisco Bay Area
Asked on: Wednesday, February 9, 2011 at 3:27 pm EST
Answered on: Tuesday, May 14, 2024 at 1:22 am EDT
Question: We have a client that would like backup power for a refrigeration unit. The FLA of the unit is 7.5a. They are requesting 10 hours of standby power. The problem is, I don't know what percentage of time the refrigeration unit runs. If the FLA is 7.5, the average draw will be less and it is only drawing that for a certain percentage of time.The manufacturer was no help. I figure I can't be the first guy to run across this. Is there a rule of thumb for this? It has to be a battery backup not a generator os over sizing gets expensive.For the record we did discuss that the refrigerator would keep things cold for a length of time even with now power. This is a laboratory where the temperature control is very important.Thanks.
Rule of Thumb for Duty Cycle
A common rule of thumb is to assume a duty cycle of 50% for refrigeration units. This means that the unit is estimated to operate about half of the time.
Calculation for Battery Capacity
Using the following formula, you can calculate the battery capacity required for 10 hours of standby power:
Battery Capacity (Ah) = (FLA x Duty Cycle) x Standby Time (h)With a FLA of 7.5 A, a duty cycle of 50% (0.5), and a standby time of 10 hours:Battery Capacity = (7.5 A x 0.5) x 10 h = 37.5 AhBattery Selection