Topic: Sizing backup power for refrigeration unit

User: sfav8r, Location: San Francisco Bay Area

Asked on: Wednesday, February 9, 2011 at 3:27 pm EST
Answered on: Tuesday, May 14, 2024 at 1:22 am EDT

Question: We have a client that would like backup power for a refrigeration unit. The FLA of the unit is 7.5a. They are requesting 10 hours of standby power. The problem is, I don't know what percentage of time the refrigeration unit runs. If the FLA is 7.5, the average draw will be less and it is only drawing that for a certain percentage of time.The manufacturer was no help. I figure I can't be the first guy to run across this. Is there a rule of thumb for this? It has to be a battery backup not a generator os over sizing gets expensive.For the record we did discuss that the refrigerator would keep things cold for a length of time even with now power. This is a laboratory where the temperature control is very important.Thanks.

Rule of Thumb for Duty Cycle

A common rule of thumb is to assume a duty cycle of 50% for refrigeration units. This means that the unit is estimated to operate about half of the time.

Calculation for Battery Capacity

Using the following formula, you can calculate the battery capacity required for 10 hours of standby power:

Battery Capacity (Ah) = (FLA x Duty Cycle) x Standby Time (h)
With a FLA of 7.5 A, a duty cycle of 50% (0.5), and a standby time of 10 hours:
Battery Capacity = (7.5 A x 0.5) x 10 h = 37.5 Ah
Battery Selection

To provide 37.5 Ah of capacity, you would need a battery with a higher Ah rating. Common battery sizes for this application are 50 Ah or 100 Ah.

Oversizing Considerations

While oversizing the battery may seem like a good idea, it does add to the cost. If the refrigerator does not run as often as the estimated 50% duty cycle, the battery may be oversized.

Other Factors to Consider



Temperature

The duty cycle can vary depending on the temperature inside the refrigerator.


Door openings

Frequent door openings can affect the duty cycle.

Manufacturer specifications

Some manufacturers may provide guidance on duty cycle or operating time.

Recommended Approach:
Consult with the refrigerator manufacturer for any specific operating data. Monitor the refrigerator's operation to determine a more accurate duty cycle. Select a battery size that provides sufficient capacity while considering the possibility of oversizing. Flag for review