Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Cable tray conection

User: MichaelJ, Location: Georgia

Asked on: Wednesday, February 9, 2011 at 3:48 pm EST
Answered on: Tuesday, May 14, 2024 at 1:22 am EDT

Question: What code section would regulate the conection from a cable tray to a MCC or a Main breaker panel? Is it allowed to cut a square hole in the top of a Main breaker cabinet and attach cable tray directly to it? Is there a listed adapter?

Code Section

[NFPA 70 (National Electrical Code) 392.3(B)](https://www.nfpa.org/Codes-and-Standards/All-Codes-and-Standards/List-of-Codes-and-Standards/National-Electrical-Code-NEC/Article-392/Section-392.3)

Allowance of Square Hole in Main Breaker Cabinet



No, it is not allowed to cut a square hole in the top of a main breaker cabinet and attach cable tray directly to it.


Section 392.3(B) of the NEC states that "Cable trays shall not be attached to the surface of electrical enclosures." This prohibition applies to all electrical enclosures, including main breaker cabinets.

Listed Adapter

There is no listed adapter that allows for the direct connection of cable tray to a main breaker cabinet.

Proper Connection Method

To properly connect cable tray to a main breaker cabinet, use one of the following methods:


Use a listed cable tray transition fitting

These fittings are designed to connect cable tray to the enclosure while maintaining the required clearances and protection from physical damage.*

Mount a separate junction box on the outside of the cabinet:
This method allows you to connect the cable tray to the junction box and then run conduit from the junction box to the main breaker cabinet. Flag for review

Previous Question Next Question