Topic: NM covered one side

User: augie47, Location: Tennessee

Asked on: Wednesday, February 9, 2011 at 6:53 pm EST
Answered on: Tuesday, May 14, 2024 at 1:23 am EDT

Question: In regard to 334.10(3), this may be answered by Appendix E, but, Appendix E and I have not come to friendly terms as of yet, so allow me to post a couple of scenarios.Condition 1: Building is typical commercial "red iron" structure. Exterior is insulated metal walls. Inside is metal studs with walls and ceiling covered one side with sheet-rock.Is Romex allowed ? (Code says "cables shall be concealed within walls, floors, or ceilings that provide a thermal barrier of material that has at least a 15-minute finish rating as identified in listings of fire-rated assemblies. "Condition 2: Same as one except sheet-rock covered room(s) are only a potion of the building (such as small offices in an open warehouse)Those walls exposed to the warehouse are coved both sides but those exposed to the exterior walls are not.I have been taught one of the reasons for the barrier was containingfumes in the event of a fire. In condition 2, any fumes would be free to fill the warehouse.In Condition, the entire building is covered one side. Fumes would onlyescape to above a sheet rock ceiling.Only one side is covered so cable is not necessarily "within"

Condition 1

Appendix E of the NEC does not address the use of Romex in commercial buildings with insulated metal walls and metal studs covered on one side with sheetrock. However, Section 334.10(3) of the NEC does require cables to be concealed within walls, floors, or ceilings that provide a thermal barrier of material that has at least a 15-minute finish rating. Insulated metal walls typically meet this requirement, and sheetrock also has a fire-resistance rating. Therefore,

Romex is likely permitted
in this scenario.

Condition 2

In this scenario, the sheetrock walls that are exposed to the warehouse do not provide a thermal barrier for the cables. Therefore,

Romex is not permitted
in this area. The cables must be installed in conduit or other approved raceways.The purpose of the thermal barrier is to contain smoke and fumes in the event of a fire. In Condition 1, the entire building is covered on one side, so fumes would only escape to above a sheetrock ceiling. In Condition 2, however, fumes could escape into the warehouse, which is a larger space and would pose a greater hazard. Flag for review